For a hydromessage bathtub can you use a stranded wire for your bonding in the 2005 code? I have the 2008 code with me but need to know what the 05 code said. Anyone?

Here is the part of the 08 reference...

680.74 Bonding. All metal piping systems and all grounded

metal parts in contact with the circulating water shall be

bonded together using a solid copper bonding jumper,

what's the 05 code say?

Link to comment
Share on other sites

For a hydromessage bathtub can you use a stranded wire for your bonding in the 2005 code? I have the 2008 code with me but need to know what the 05 code said. Anyone?

Here is the part of the 08 reference...

680.74 Bonding. All metal piping systems and all grounded

metal parts in contact with the circulating water shall be

bonded together using a solid copper bonding jumper,

what's the 05 code say?

Ah! My error! My earlier post was incorrect. I broke my own rule and didn't read the entire paragraph carefully.

The '05 edition says:

680.74 Bonding. All metal piping systems and all grounded metal parts in contact with the circulating water shall be bonded together using a copper bonding jumper, insulated, covered, or bare, not smaller than #8 AWG solid.

This doesn't exactly say that the wire has to be solid, the wire just has to be no smaller than #8 AWG solid. I suppose that the new wording clarifies the intent that the wire should actually be solid.

- Jim Katen, Oregon

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

 Share

×
×
  • Create New...