Jump to content

Recommended Posts

Posted

Is this considered bundling? The issue of bundling cables has been discussed here before, does it apply to individual conductors like this? This is inside the main panel.

Click to Enlarge
tn_2009916234727_P9163680%20copy.jpg

22.69 KB

Posted

Is this considered bundling? The issue of bundling cables has been discussed here before, does it apply to individual conductors like this? This is inside the main panel.

If the bundle is shorter than 24" it's not an issue.

310.15(B)(2)(a) blah, blah, blah, where single conductors . . . are stacked or bundled longer than 24" without maintaining spacing and are not installed in raceways, the allowable ampacity or each conducotr shall be reduced as shown in blah, blah, blah."

I can't find any prohibition against stacking or bundling single conductors for a distance of 24" or less.

- Jim Katen, Oregon

Posted

Hi Randy,

It looks like that's in a panel, the sheathing has been removed, and the electrician wrapped the hots and neutrals together.

I'm waiting to see what Jim thinks about the installation.

I see it now. I wasn't "seeing" the scale of the wires to the panel in the pic.