Yes Erik with a K, NOT LESS THAN therefore it needs to be 5' or MORE away from the hot tub. The link you posted above does not apply because this is a SFR and the answer in the link does not qualify SFR. Most of these jobs are with PVC and THWN pulled inside. I just did a job for my aunt like this 2 weeks ago. I pulled NM inside the house and from the exterior disco to the hot tub I pulled THWN, 6/3NM inside the house and #8 THWN outside the house and was able to maintain the 50A required rating.. NEC 110.14©(1)(a)(1) states; (a) Termination provisions of equipment for circuits rated 100 amperes or less, or marked for 14 AWG through 1 AWG conductors, shall be used only for one of the following: (1) Conductors rated 60°C (140°F). #8 is rated 40A @ 60C You left out this part: (3) Conductors with higher temperature ratings if the equipment is listed and identified for use with such conductors. (4) For motors marked with design letters B, C, or D, conductors having an insulation rating of 75°C (167°F) or higher shall be permitted to be used, provided the ampacity of such conductors does not exceed the 75°C (167°F) ampacity.