I belong to the NFPA and get an NEC newsbrief newsletter. There is always a question that the NFPA officially answers. I thought this one was a no brainer but the detailed, long answer was enlightening. Question: Can 14-2 wire be used for the switch leg of a light fixture where the branch circuit is protected by a 20-amp circuit breaker? If this is prohibited by the Code, why can 15-amp switches and receptacles be used on 20-ampere circuits? Answer: The conductors from a switch location to the lighting outlet it controls are considered branch-circuit conductors, not tap conductors connected to branch-circuit conductors. These conductors are subject to the general overcurrent protection requirements of 210.20(B), which points to 240.4 for the specific overcurrent protection requirement. Section 240.4(D) specifies that 14 AWG copper conductors are to be protected by an overcurrent protective device with a rating or setting no higher than 15 amperes. Table 210.24, which summarizes the requirements for branch circuits with two or more outlets or receptacles, specifies that the minimum conductor size for a 20-ampere-rated branch circuit is 12 AWG. Section 210.21(B)(3) permits a 15-ampere receptacle to be connected to a 20-ampere rated branch circuit. The terminals of feed-through type receptacles rated 15 amperes are tested for the heating that will result from the full load of a 20-ampere branch circuit. In addition, the attachment caps of cord-and-plug-connected appliances are configured based on the appliance load. If the appliance is rated greater than 15 amperes, its cord cap will not be compatible with the configuration of a 15-ampere receptacle. Snap switches installed on branch circuits are subject to the load requirements specified in 404.14. For ac general-use snap switches controlling resistive or inductive lighting loads, the minimum rating cannot be less than the load it supplies. In other words, a 15-ampere switch installed on a 20-ampere circuit can supply a load of 15 amperes. For switches controlling lighting outlets supplied by 15- and 20-ampere branch circuits, it is the load controlled by the switch and not the rating of the branch circuit that determines the switch's minimum ampere rating.