Dangerous ground connection? Opinins please...


Goodhome

Recommended Posts

Hello everyone,

I came across this at an inspection today. It appears that the ground is attached to the gas line. Any opinions would be much appreciated.

Thanks,

Sean

Click to Enlarge
tn_201152001512_Gas%20line%20ground.jpg

59.45 KB

Looks like a bonding connection to the gas line. Since CSST is present, the gas lines are *required* to be bonded to the electrical system with #6 copper.

Are you aware of the difference between grounding and bonding?