Jump to content

Gas Water Heater Clearance


gpruett

Recommended Posts

Question, does anyone know what the draft hood clearance should be for a gas fired WH from combustibles? Found an attic install today where the draft hood was 5" from the roof decking. I know about the 1" rule on the flue, but can't find anything specific about the top clearances. Thanks folks!

Link to comment
Share on other sites

I can't imagine how the draft hood could be so close to the roof; there would barely be any room for a flue. I would consider the draft hood the same as a single wall flue- six inches of clearance. There is also the required clearance from the top of the heater itself, which I believe is twelve twelve inches.

All of the clearances are printed on the newer water heaters.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...