panel ground / made electrode


jodil

Recommended Posts

I just want confirmation for my thoughts here. The ground for the main panel is attached to the closest water line about 6 feet from the water meter. There is no jumper at the meter becuase the main supply line is PVC.. so the ground should be attached somewhere else since the ground cant actually get to the "ground" right?

thanks

Link to comment
Share on other sites

I just want confirmation for my thoughts here. The ground for the main panel is attached to the closest water line about 6 feet from the water meter. There is no jumper at the meter becuase the main supply line is PVC.. so the ground should be attached somewhere else since the ground cant actually get to the "ground" right?

Sort of right. The wire from the main panel to the water piping is for bonding of the water piping system not grounding of the service equipment. The service equipment has to be connected to a grounding electrode system. That GES has to include all available grounding electrodes. That should include, most notably, the foundation steel if it's a newer building. If it's an older building, then, yes, someone should drive a pair of ground rods.

- Jim Katen, Oregon

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...