Aluminum service entry in to the main service panel, 200 amp CH. It appears that someone tapped into the main disconnect (double tapped?) to feed a sub-panel about 6 ft away. It is a 125 amp. My question is, Is this allowed?

Click to Enlarge
tn_2011121171218_100_4857.jpg

61.46 KB

Click to Enlarge
tn_2011121171435_100_4856.jpg

52.86 KB

Share this post


Link to post
Share on other sites

No it is not allowed. The manufacturer of that main breaker would have to list it as allowing multiple circuits and I do not think it is listed as such.

Share this post


Link to post
Share on other sites

I think taps are allowed but not in the manner shown in the photo. A gutter box and listed tap connectors are needed.

Marc

Share this post


Link to post
Share on other sites

As you know, the correct way to feed a 125 amp subpanel is by way of a 125 amp breaker installed below the main breaker. If you tap the service above, it isn't really a sub, is it?

Besides the double taps, the way the insulation was not stripped completely on those branch circuit cables coming in at the top suggest the work was done by a DIYer without a permit. I can't see if cable clamps were used.

(In Canada, branch circuits are not permitted in that close proximity to the main conductors. It is allowed in the US, but why not keep them clear of the service conductors if possible?)

Another thing, the drywall is brought in over the edges of the panel. That is wrong. The panel box should be flush with the surface of the wall so that the cover can fit tight. If there is ever a fire in there, it needs to be contained.

Share this post


Link to post
Share on other sites

As you know, the correct way to feed a 125 amp subpanel is by way of a 125 amp breaker installed below the main breaker. If you tap the service above, it isn't really a sub, is it?

The panel bus stabs may not be listed to use a 125A breaker, they may be only rated for 110A max. (110A is a standard rating).This is just another reason to read the labels on a panel.

Share this post


Link to post
Share on other sites

Of course there are at least 4 other double taps on the left side, white wires being used as hot wires to breakers, and other issues. Get sparky in there to fix all issues.

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Sign in to follow this  

×
×
  • Create New...