Brandon Whitmore Posted January 22, 2012 Report Share Posted January 22, 2012 Anyone have a code cite showing the min. clearance requirement for an oil tank vent and fill pipe to a window/ door? If I find it first, I'll post up....... Quote Link to comment Share on other sites More sharing options...
Brandon Whitmore Posted January 22, 2012 Author Report Share Posted January 22, 2012 Answer: NFPA 31..... (8.6.2)-- 2' from any building opening. Quote Link to comment Share on other sites More sharing options...
Bill Kibbel Posted January 23, 2012 Report Share Posted January 23, 2012 This was also covered in the discussion on a similar topic (that you started several months ago). https://www.inspectorsjournal.com/forum ... C_ID=14644 Quote Link to comment Share on other sites More sharing options...
Brandon Whitmore Posted January 23, 2012 Author Report Share Posted January 23, 2012 That pretty much seals it. I think I'm losing brain cells at a very quick pace. Alzheimers may kick in before I turn 40 at this rate. The scary thing is that I remembered it being 3'- probably due to the 3' requirements for nat. gas vents. I think that was the last time I inspected a house with an above ground fuel storage tank. On this inspection I got to write up the fact that the tank was within 7' of the burner-- a first for me. Quote Link to comment Share on other sites More sharing options...