NBHI Oregon Posted September 16, 2020 Report Share Posted September 16, 2020 I did an inspection today of a commercial building. The inspection consisted of only the electrical and the foundation. While in the panels I noticed that there were many breakers but only a few ground wires. It seemed really really odd to me. Quote Link to comment Share on other sites More sharing options...
Jim Katen Posted September 16, 2020 Report Share Posted September 16, 2020 They're using the EMT as the equipment grounding conductor. Quote Link to comment Share on other sites More sharing options...