BADAIR Posted May 19, 2006 Report Share Posted May 19, 2006 Grounding of equipment and bonding of all permanent installed metallic items in and around pools is always a concern of mine. What do you think and say about metal downspout within 4' and metal guttering/roof drip edge within 8'6" as depicted? Download Attachment: Metalgutterpool.JPG 94.93 KB Quote Link to comment Share on other sites More sharing options...
mcramer Posted May 21, 2006 Report Share Posted May 21, 2006 Originally posted by BADAIR Grounding of equipment and bonding of all permanent installed metallic items in and around pools is always a concern of mine. What do you think and say about metal downspout within 4' and metal guttering/roof drip edge within 8'6" as depicted? Download Attachment: Metalgutterpool.JPG 94.93 KB The downspout requires bonding. Quote Link to comment Share on other sites More sharing options...
PAbernathy Posted February 17, 2007 Report Share Posted February 17, 2007 (5) Metal Wiring Methods and Equipment. Metalsheathed cables and raceways, metal piping, and all fixed metal parts except those separated from the pool by a permanent barrier shall be bonded that are within the following distances of the pool: (1) Within 1.5 m (5 ft) horizontally of the inside walls of the pool (2) Within 3.7 m (12 ft) measured vertically above the maximum water level of the pool, or any observation stands, towers, or platforms, or any diving structures Yep, in this picture it should be bonded. Quote Link to comment Share on other sites More sharing options...