Just did an inspection for a one year warranty. Typical meter main installation with a distribution panel in the garage. The neutral and ground bus bars were not bonded together, but the neutral wires running off the AFCI breakers were attached to the ground bus bar. This seems like an improper installation to me, but was wired by an electrician and signed off by the city inspector. -- can anyone tell me whether or not this is allowed?

Thanks

Link to comment
Share on other sites

Originally posted by Brandon Whitmore

Just did an inspection for a one year warranty. Typical meter main installation with a distribution panel in the garage. The neutral and ground bus bars were not bonded together, but the neutral wires running off the AFCI breakers were attached to the ground bus bar. This seems like an improper installation to me, but was wired by an electrician and signed off by the city inspector. -- can anyone tell me whether or not this is allowed?

Thanks

If you're talking about the little coiled white wire that comes out of the AFCI device, you're correct. It's supposed to be connected to the neutral bar, not the grounding bar.

The printed instructions are very clear on the matter.

- Jim Katen, Oregon

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...