Chris Bernhardt Posted July 31, 2007 Report Share Posted July 31, 2007 Is there zip cord rated for exterior use and is it an approved wiring method for exterior mounted light fixtures? Image Insert: 49.08 KB Chris, Oregon Quote Link to comment Share on other sites More sharing options...
Chris Bernhardt Posted July 31, 2007 Author Report Share Posted July 31, 2007 Oops, never mind. Dam thing suppose to be grounded, so the answer should be no, its wrong. I should get some sleep. Chris, Oregon Quote Link to comment Share on other sites More sharing options...
Jim Katen Posted July 31, 2007 Report Share Posted July 31, 2007 Originally posted by Chris Bernhardt Oops, never mind. Dam thing suppose to be grounded, so the answer should be no, its wrong. I should get some sleep. Chris, Oregon First, in addition to the grounding problem, branch circuits aren't supposed to be wired with anything less than #14. (310.5) Next, while zip cord has some legitimate uses -- pendants for instance -- it must always be installed in a dry location. (T 400.4) Lastly, 400.8 contains a laundry list of things you're not supposed to do with cord and that picture shows several of them. (Substitute for the fixed wiring of a structure; run through holes in walls; attached to building surfaces; portions concealed by walls; subject to physical damage; etc, etc.) - Jim Katen, Oregon Quote Link to comment Share on other sites More sharing options...
Chris Bernhardt Posted July 31, 2007 Author Report Share Posted July 31, 2007 Thanks Jim! Chris, Oregon Quote Link to comment Share on other sites More sharing options...