JohnC Posted April 24, 2012 Report Posted April 24, 2012 Just checking to be sure I have my facts right. The electrical panel has six double taps, labels hard to read. When I blew up the photos the top photo is rated for one wire and bottom photo rated for two wires. So am I outstanding this properly, that two wires are okay for the circuit rate for two wires? The other labels I could not read. John Callan Click to Enlarge 56.78 KB Click to Enlarge 69.74 KB
Jim Katen Posted April 24, 2012 Report Posted April 24, 2012 All of the breakers in each of your pictures can have either one or two wires secured under the lugs.
JohnC Posted April 24, 2012 Author Report Posted April 24, 2012 Thanks Jim, I just looked at the two photos again more closely and see this now. Just shows you have to be carefully calling out double taps.-Thanks-I may need an eye exam! John Callan
Jim Katen Posted April 24, 2012 Report Posted April 24, 2012 I know, the printing on those things is ridiculous. You need a jeweler's loupe to read them sometimes.
Jerry Simon Posted April 24, 2012 Report Posted April 24, 2012 I haven't taken a doube tap since college. . .
Recommended Posts
Create an account or sign in to comment
You need to be a member in order to leave a comment
Create an account
Sign up for a new account in our community. It's easy!
Register a new accountSign in
Already have an account? Sign in here.
Sign In Now