Came across an a-coil condensate line that was developing condensation. The condensation was on about 24" of the PVC closest to the a-coil located in the attic space. Initially, I thought it was a small leak at the bottom of the line and the water was clinging to the pipe from adhesion and following the slope. But I could not pinpoint a leak. I've never come across this before and wonder what, if any, malfunction it could represent since the A/C seemed to be functioning correctly. I recorded an 18 degree drop with an IR camera at the register closest to the coil. It was not exceptionally hot in the attic space about 90-100 degrees and it was well ventilated. Outside temperature was about 75 degrees.

Link to comment
Share on other sites

Many manufacturer require/request that the first 24-inches of the primary condensate line from the EVAP coil be insulated.

This to minimize/contain the sweating of the PVC.

Of course in Texas in many/most cases the furnace/EVAP coil are located in the attic and the summer temps can range from 130 to 170 degrees and thus a lot of sweating from the condensate line.

Sweating results in the water/moisture soaking through the insulation and then the ceiling sheetrock and then folks freaking out thinking they have roof leaks.

And ... we don't always see the insulation wrap on the condensate lines down here as well.

Link to comment
Share on other sites

Thanks Jim always very informative:) I could understand seeing condensation in a high humidity area like Texas but with relative humidity between 40%-60% here in Santa Barbara and a low attic temperature, I would not expect to see condensation develop as I never have before. Just wanted to be sure it wasn't indicative of some other defect like a clogged line or something like that.

Link to comment
Share on other sites

Thanks Jim always very informative:) I could understand seeing condensation in a high humidity area like Texas but with relative humidity between 40%-60% here in Santa Barbara and a low attic temperature, I would not expect to see condensation develop as I never have before. Just wanted to be sure it wasn't indicative of some other defect like a clogged line or something like that.

Nah, you just happened to catch it at a good moment. I expect that most of your uninsulated condensate drains sweat now & then under the right conditions of temperature and humidity.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...