mridgeelk Posted April 9, 2008 Report Share Posted April 9, 2008 Does this brick chimney (with issues of its own) location in relation to the furnace vent represent "a vertical wall or similar obstruction" as in G2427.6.3 #2 of the 2006 IRC and should be terminated two feet above the chimney? I told my clients that it was short but I wasn't sure how much. Thanks for any replies. Ed Image Insert: 342.2 KB Link to comment Share on other sites More sharing options...
hausdok Posted April 9, 2008 Report Share Posted April 9, 2008 Hi, Well, without looking it up, I believe the requirement is two feet above any vertical sidewall within 8 ft., but I'm not so certain that a chimney that's only about 2ft. on a side will make that much difference, but it will cost very little to add another 3-4ft. to that vent and install some guy wires. That's what I'd write. OT - OF!!! M. Link to comment Share on other sites More sharing options...
Jim Katen Posted April 9, 2008 Report Share Posted April 9, 2008 Originally posted by mridgeelk Does this brick chimney (with issues of its own) location in relation to the furnace vent represent "a vertical wall or similar obstruction" as in G2427.6.3 #2 of the 2006 IRC and should be terminated two feet above the chimney? You betcha. - Jim Katen, Oregon Link to comment Share on other sites More sharing options...
Brandon Whitmore Posted April 9, 2008 Report Share Posted April 9, 2008 You betcha. Dang it, I read the exact opposite on another forum a while back. Link to comment Share on other sites More sharing options...
RickSab Posted April 9, 2008 Report Share Posted April 9, 2008 Here's my two cents. It is 2" higher than any part of the building within 10" Any yes there are issues with that brick Chimney. Rick Link to comment Share on other sites More sharing options...
msteger Posted May 8, 2008 Report Share Posted May 8, 2008 Originally posted by mridgeelk Does this brick chimney (with issues of its own) location in relation to the furnace vent represent "a vertical wall or similar obstruction" as in G2427.6.3 #2 of the 2006 IRC and should be terminated two feet above the chimney? I told my clients that it was short but I wasn't sure how much. Thanks for any replies. Ed Image Insert: 342.2 KB Definitely an issue. Violates the 10-2-3 rule. Link to comment Share on other sites More sharing options...
Brandon Whitmore Posted May 9, 2008 Report Share Posted May 9, 2008 Definitely an issue. Violates the 10-2-3 rule. Based on memory the requirement for a chimney is the 10-2-3 rule. For a B vent, there is no 10-2-3 rule. The requirement is based on the slope of the roof (min. 12"). The 2' above the roof line within 10' applies when there is a sidewall within 8' horizontal feet of a sidewall. I am still not fully convinced that the B vent needs to be extended..... I am curious as to why there is a requirement to go 2' above any point within 8' horizontally of a sidewall, when there is only a 12" requirement elsewhhere. The only thing I can think of is that there would be a chance of venting back through an eave vent or window?? Anyone have an idea or answer? Link to comment Share on other sites More sharing options...
Jim Katen Posted May 9, 2008 Report Share Posted May 9, 2008 Originally posted by Brandon Whitmore . . . I am curious as to why there is a requirement to go 2' above any point within 8' horizontally of a sidewall, when there is only a 12" requirement elsewhhere. The only thing I can think of is that there would be a chance of venting back through an eave vent or window?? Anyone have an idea or answer? I believe that it's related to turbulence. When the wind blows against a wall, it creates turbulence that can interfere with the drafting of a B-vent. I suspect that the same thing would happen with the chimney in the OP. - Jim Katen, Oregon Link to comment Share on other sites More sharing options...
msteger Posted May 9, 2008 Report Share Posted May 9, 2008 Originally posted by Brandon Whitmore Definitely an issue. Violates the 10-2-3 rule. Based on memory the requirement for a chimney is the 10-2-3 rule. For a B vent, there is no 10-2-3 rule. The requirement is based on the slope of the roof (min. 12"). The 2' above the roof line within 10' applies when there is a sidewall within 8' horizontal feet of a sidewall. I am still not fully convinced that the B vent needs to be extended..... I am curious as to why there is a requirement to go 2' above any point within 8' horizontally of a sidewall, when there is only a 12" requirement elsewhhere. The only thing I can think of is that there would be a chance of venting back through an eave vent or window?? Anyone have an idea or answer? Is the chimney 2' taller than anything within 10' of it? Doesn't look like there is a 24" difference b/w that and the metal vent next to it. Link to comment Share on other sites More sharing options...
Brandon Whitmore Posted May 9, 2008 Report Share Posted May 9, 2008 Is the chimney 2' taller than anything within 10' of it? Doesn't look like there is a 24" difference b/w that and the metal vent next to it. Either way, it does not appear to be 3' through the roof as it should be. Link to comment Share on other sites More sharing options...