Paul MacLean
    344
Everything posted by Paul MacLean
  1. I work it in reverse. I use the 3-light tester and pull out the SureTest when something's suspicious. I try to check every accessible receptacle in the house, so using the SureTest on all of them would be a burden.
  2. Same here, but I can't remember the last time I saw a fuse panel. I also test trip the AFCI breakers in new construction (vacant house) but I don't trip them in and occupied house because I don't know what's on the circuit.
  3. First a disclaimer...electricity is not my strong suit. In Central Texas we have one rural electric co-op that uses a similar set-up. The meter and main disconnect are located at a pedestal in the front yard utility easement with a three wire feeder to a service panel located on the house. In newer homes, the house panel is wired as main service panel with a main disconnect, neutral & grounds bonded and its own ground rod, etc. This I think is OK. In older properties, the house panel is frequently wired with neutrals and grounds bonded, no main disconnect and no ground rod. I always write up the older houses saying that this is technically a subpanel and doesn't conform with my understanding of the NEC and recommend a sparky check it out and make any necessary repairs. Do one has ever argued with this write-up. I have never been able to get a clear explanation of this, except that the utility company isn't bound by the NEC. However, the trend to a whole new main service entrance panel on the newer houses suggests to me that electricians are beginning to see it as I do. Doug Hansen...are you out there?
  4. My experience exactly. I had a rubber one burst on me 25 years ago and it flooded the entire first floor. I have also seen the "aneurysms" Jim mentioned. I always recommend the braided hoses (verbally, not in my report) to clients. It's about the cheapest insurance you can buy.
  5. I've never seen one around here, but I vote with Kurt. Cistern is my guess.
  6. Mike. Thanks again! iespell.com only works when you use it...duh.
  7. Mike, I just noticed a typo in the description under my link. How do I edit it? Thanks!
  8. Mike said, "That's odd. If I'm not mistaken, Paul MacLean has had one of those for years and years. Paul, you out there? Is that the same brand?" Yeah, Mike. I'm hanging in out here. I bought my "Amazing Telescopic Ladder" from CSS Inc. in Birmingham, MI in August, 1996. I use it almost daily. I learned quickly that I had to keep it clean and that it requires regular maintenence. The instructions said to use "lemon oil based dusting/cleaning spray". That didn't work worth a sh*t. I started using WD 40. The WD 40 is messy, acumulates aluminum dust on the sides and makes your hands black. (So, don't hold onto the sides.) The WD 40 also eventually deteriorated the nylon (?) guides that keep the sections from pulling apart. Today most sections of my ladder will pull completely apart. And occasionally the bottom section sticks and I have to get rough with it. Once it was so stuck I used an automotive jack to pull it apart. But when cleaned up, it still works fine. I have less problems in warm weather than in cool weather. The ladder's convenience over-shadows the difficulties and I frequently tell clients it's the best tool I ever bought. I can't imagine doing inspections without it. A few months ago, I decided it was time to get a new Telesteps ladder. I ordered one through Amazon.com. I got a notice that there were delivery problems and thought "screw it". I going to stick with the ladder I have as long as I can make it work.
  9. That's right sports fans. Members of CREIA and TAREI need not take the NHIE to become ASHI members. This may start a new thread, but it is a bit of a bombshell that most ASHI members are not aware of and I thought it merited highlighting. Jim, I'm not sure about CREIA, but for a TAREI member to be accepted as an ASHI Member he has to have TAREI's CPI (Certified Professional Inspector) designation. That means over 1000 inspections and passing a test. The current CPI test is ICC code certification. I'm a ASHI Member, but I am not a TAREI CPI member. Few TAREI members are CPIs. Another catch for the TAREI CPI is that his reports must meet ASHI SOP. There are enough differences that the TAREI CPI would probably have to change his reporting format. While all the TAREI CPIs I know are well qualified to be ASHI Members, I doubt that many will jump on board. These guys don't need ASHI.
  10. As an ex APA Field Rep (1968 to 1974)I know APA - The Engineered Wood Association has done extensive testing of plywood roof decking and 5/16" on 16" centers it is plenty strong structurally. It does give under foot and that is one of the reasons for ply-clips between supports. The ply-clips keep the panel edges moving together to help keep from tearing shingles. The one weakness I see to 5/16" decking is the holding power of shingle nails. 3/8" decking is better. I don't see any 5/16" decking here, but I do see a lot of 3/8" decking on 24" centers in Central Texas. Occasionally a client will complain about give or a spongy feeling when he walks the roof, but I have never seen a performance failure. I left APA before they got into OSB. I my APA days we used to badmouth OSB type products, but that was before APA members started making it. Now they promote it. APA is a reliable, reputable group and you can take their recommendations to the bank. My opinion. Worth what you paid for it.
  11. OK, the non-technical guy is going to jump into this. It's my understanding that insulation in contact with the metal flue can cause hot spots in the flue and damage the flue pipe. In any case, at least 1-inch clearance is needed between the the flue and surrounding insulation.
  12. I'll add an insulated screwdriver to Bruce's shoes and glasses. But this is stuff I use for everything, so I am not taking special precautions. I do take a good look at the panel before removing the cover to be sure there are no obvious problems. Years ago, I put a pointed screw into a hot wire replacing the cover. That was exciting. Sparks flew and the breaker tripped. I recommended an electrician make repairs and was never asked to pay anything.
  13. What a bummer! To make things worse, you now have a water problem listed on you house's CLUE report. A CLUE (Comprehensive Loss Underwriting Exchange) report lists its claim history for the past five years. CLUE reports are available only to homeowners and the insurance industry. CLUE reports include every claim inquiry or report by a homeowner, even if it didn't result in a loss payment.
  14. Jim...we hope it's open ended![:-timebm]
  15. Katen said "Remember that a class 200 electric meter is actually rated for a maximum load of 250 amps. The "200" designation is 80% of its maximum capacity, often called its "continuous rating" because it's rated to pass 80% of its full load "continuously." That's exactly what I was looking for. The SEC and main breaker supported 225 amp service, but I didn't know about the meter ratings.
  16. On a 1997 large house yesterday I found a meter marked 200CL and the service entrance panel was rated for 225 amps with a 225 amp main breaker. Is this a problem? If so what would you say? Thanks!
  17. A couple of web sites: Aluminum Wiring in Residential Properties -- http://www.inspect-ny.com/aluminum.htm “Repairing Aluminum Wiringâ€
  18. Here's a brief statement about the Ideal Purple Wire Nut. This is the only wire nut I am aware suitable for copper/aluminum use. "Ideal Purple Wire-nuts: Some of the test info includes this abstract from a paper presented at the IEEE Holm Conference on Electrical Contacts, Jan 1997: Abstract: A new type of twist-on splicing component for use with aluminum and copper wire combinations is tested to determine initial resistance, peformance in a zero-current environment test, performance in a heat-cycle test, and portion of current carried by the connector's steel spring. The splices tested consist of two aluminum wires and one copper wire. The aluminum wire samples used for the test are of the types actually installed in aluminum-wired homes. Initial resistance is found to be relatively high, and there is a significant sample-to-sample variation. This reflects failure to consistently establish low-resistance wire-to-wire contact through the insulating oxide film on the wire. Results of the environmental and heat-cycle tests show deterioration of a significant portion of the samples. The splices made with this connector are also found to be sensitive to mechanical disturbance, such as applied in normal installation when the completed splice is pushed back in to the junction box. Based on the test results, it is concluded that this connector has not overcome the fundamental deficiency of twist-on connectors for use with aluminum wire applications." Also the CPSC considers the Ideal Purple Wire Nut good for only temporary repairs, not permanent repairs.
  19. For years I used to write any plastic T&P drainpipe as "not rated for 210 degrees or 150psi, the temperature and pressure at which the T&P valve opens." I took a lot of grief and got slapped around by codes permitting CPVC (as others have stated). So I backed off and don't make such a big deal about it any more. I just make sure the CPVC isn't close to the flue and discharges correctly. I have yet to see PEX on a water heater; in fact, seeing PEX at all is very rare around here.
  20. If your not already a subscriber (no charge) to Mike Holt's newsletters, stray voltage and lots of other great electrical and NEC information is discussed. Go to: http://68.225.22.180/index.php?id=homegeneral and explore.
  21. My ride is a '97 Ford Ranger with a rack to carry my 24' extension ladder. I guess I'm lucky in my area because it has only 85,000 miles on it. I'm going to nurse it another 2 years then retire. My Ranger is a 4 banger, but if I had it to do over I'd buy a 6. Another inspector I know has the Honda Element. It looks great and he says he loves it. Hummer...bummer!
  22. Long before my home inspection days, I drove into Del Rio, Texas the day after a hail storm...soft ball size hail that is. What a mess!
  23. Donald, FWIW I don't call out gas valves behind ranges, dryers, etc. I do call'em out if they are out of reach and the appliances can't be moved for access (i.e. a water heater). Besides, unloading the cabinet beside the range to get to the gas valve is more trouble than moving the range...
  24. Well thanks Scott![!] That's all we need in Austin is another fur-in-ner invasion. We have imported carp to eat the duck weed in the lakes, hunters to kill the deer in the garden and fireants to help keep the fur-in-ners out. All to no avail. Now you want to send us Kudzu...geez. Truthfully, I spent about ten months in Jackson, Yazoo City and the rest of Mississippi in 1988. Until then I had never heard of Kudzu. Now I know it on sight. I preferred the Natchez Trace. Y'all come to Austin! It's a great place to visit, spend a few dollars and then go home...[:-bigeyes]...what am I saying. I make my living off all those folks moving to Central Texas.
  25. What Donald said. Here the T&P drainpipes and the pan drainpipes are plumbed separately to the exterior. Frankly, I've never seen the water heater in the attic cause a problem, but I've seen lots of ceiling damage from AC's in the attic. I take it back. My son had to have his attic water heater replaced and the plumber stepped through the ceiling trying to get the new one up there. Call out the lack of a safe walkway and work platform. I write up missing walkways and platforms all the time.