Does anyone know the origin of the convention which places a disconnect for the oil burner at the top of the basement stairs?

Yesterdays inspection had one (1997), my parents had one (1914), but I've seen others both older and newer that only had the service disconnect on the furnace cabinet (required).

Just curious.

Link to comment
Share on other sites

NFPA 31 requires 2 disconnects*.

One is a "service disconnect switch" that is within easy reach of the service tech.

The other is a labelled switch near the entrance to the room where the burner is located. An unfinished basement is the "room", so near the entrance at the top of the stairs is the required location.

*The remote disconnect does not have to be an electrical switch, if there is a way to manually stop the flow of oil to the burner, located at a safe distance from the burner.

Link to comment
Share on other sites

Thanks Jim and Bill.

I am trying to figure out how or if NFPA 31 is incorporated in the Md Fire code. One assumes it may have been at one time or may still be, hence the many installations that have two disconnects.

My 2006 copy of the MD fire code only shows it incorporates NFPA 1, Uniform Fire Code (2006 Edition) and NFPA 101, Life Safety Code (2006).

So, does anyone have a quick synopsis of how these publications fit together or are organized?

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...