Denray Posted June 1, 2012 Report Posted June 1, 2012 The panel on the left must be a cut off, but the panel on the right with over current protection should be the main panel, correct? But, it has more than 6 throws to shut off the power. Click to Enlarge 53.28 KB Click to Enlarge 62.66 KB
Jim Katen Posted June 1, 2012 Report Posted June 1, 2012 Where does the power come in from the meter? Do you have a picture of the lower right panel with its cover off?
Denray Posted June 1, 2012 Author Report Posted June 1, 2012 Just these three. Click to Enlarge 76.24 KB Click to Enlarge 84.6 KB Click to Enlarge 82.04 KB
Denray Posted June 1, 2012 Author Report Posted June 1, 2012 The meter is on the outside of that garage wall. Click to Enlarge 60.97 KB
Richard Moore Posted June 1, 2012 Report Posted June 1, 2012 Denny, the disconnect doesn't need to be an OCPD (breaker, etc) so that single shut-off lever does qualify as the service disconnect and, obviously, is less than 6 throws. It looks like you have grounding, bonding and other old house wiring issues but, with that disconnect, the number of throws is not the current problem.
Denray Posted June 1, 2012 Author Report Posted June 1, 2012 Thank you guys. I'll now let the writing begin.