Mike Lamb Posted December 16, 2012 Report Share Posted December 16, 2012 I was looking at the specs for a horizontal fan assisted water heater vent and it did not mention that the pitch needs to be upwards. Does it? The specs I was looking at merely says, "horizontal." I did not see a tag for this particular fan. This horizontal vent was about 15' with some downward and negative pitch runs. Click to Enlarge 52.79 KB Quote Link to comment Share on other sites More sharing options...
Mike Lamb Posted December 17, 2012 Author Report Share Posted December 17, 2012 I talked briefly to a rep from Tjurnlund. The vents do not need an upward slope with their in-line inducement fans. Quote Link to comment Share on other sites More sharing options...
Jim Katen Posted December 17, 2012 Report Share Posted December 17, 2012 I talked briefly to a rep from Tjurnlund. The vents do not need an upward slope with their in-line inducement fans. So where does the condensate go? Quote Link to comment Share on other sites More sharing options...
Mike Lamb Posted December 17, 2012 Author Report Share Posted December 17, 2012 Wouldn't it go out at the vent termination? Quote Link to comment Share on other sites More sharing options...
Brandon Whitmore Posted December 18, 2012 Report Share Posted December 18, 2012 As long as there is no belly in the line, it should be good to go...... Quote Link to comment Share on other sites More sharing options...