Sewer Clean-Out Inside House


Mike Lamb

Recommended Posts

Division 29 Chapter 18 is about as close as I can get....... Highlighting at end seems to address the issue....sort of....

18-29-708.3.5 Building drain and building sewer junction.

There shall be a cleanout near the junction of the building drain and the building sewer. The cleanout shall be either inside or outside the building wall and shall be brought up to the finished ground level or to the basement floor level. An approved two-way cleanout is allowed to be used at this location to serve as a required cleanout for both the building drain and building sewer. The cleanout at the junction of the building drain and building sewer shall not be required if the cleanout on a 3-inch (75 mm) or larger diameter soil stack is located within a developed length of 10 feet (3.05 m) of the building drain and building sewer connection.