Mike Lamb Posted July 12, 2015 Report Share Posted July 12, 2015 I feel I have asked this before but can't remember the answer. Is it OK to run wires back through the SEC conduit and through the meter box? Quote Link to comment Share on other sites More sharing options...
Marc Posted July 13, 2015 Report Share Posted July 13, 2015 230.7 Conductors other than service conductors shall not be installed in the same service raceway or service cable. There are two exceptions: Grounding/bonding conductors and load management control conductors having overcurrent protection. Marc Quote Link to comment Share on other sites More sharing options...
Mike Lamb Posted July 13, 2015 Author Report Share Posted July 13, 2015 Thanks. Quote Link to comment Share on other sites More sharing options...