Vent size reduction


Denray

Recommended Posts

Where it freezes, the vent diameter must be at least three inches to prevent frost closure. 

I'm not bothered by the change in size and I couldn't find anything that prohibits it- if water is running down the pipe it flows from smaller to larger. What probably limits the size is the number of fixture units. If I'm right and that's 2-1/2 inch pipe, just 6 FU's are allowed. If it's 3-inch pipe 12 FU's are allowed and it's probably OK for any normal modest house.

All that said, it probably works fine.

 

vent size.PNG

Link to comment
Share on other sites

28 minutes ago, Chad Fabry said:

Where it freezes, the vent diameter must be at least three inches to prevent frost closure. 

I'm not bothered by the change in size and I couldn't find anything that prohibits it- if water is running down the pipe it flows from smaller to larger. What probably limits the size is the number of fixture units. If I'm right and that's 2-1/2 inch pipe, just 6 FU's are allowed. If it's 3-inch pipe 12 FU's are allowed and it's probably OK for any normal modest house.

All that said, it probably works fine.

 

vent size.PNG

Chad,

Probably should stick with the standard abbreviation D.F.U., well, cuz FU.  

  • Like 2