opinions needed for giant junction box


zeb

Recommended Posts

Hi,

Well, it's busy, but it doesn't look like it violates the fill limitation. Hope they've got one or two screws securing that cover in place. A little quibble with the wiring attachment, though, The NM needs to be secured within a foot of where it enters that box, so there are quite a few wires where they screwed that up. Then you've got the large number of wires under that clamp on the upper right. Because it's out in the air and can cool readily, I'm not sure whether that violates the 'no more than 4 bundled' rule. Jim?

ONE TEAM - ONE FIGHT!!!

Mike

Link to comment
Share on other sites

I was educated by a really smart electrician once when I asked the question "How many wires, space, etc.?".....

He answered, "The amount of wiring allowed is that which fits easily & comfortably", or something like that.

I know that will bother the folks that memorize C&V, but there's a certain nice sense to it.

Link to comment
Share on other sites

Wires do require a specific amount of space for dissipating heat in a junction box.

#14 awg. 2 cu. in.

#12 awg. 2.25 cu. in.

#10 awg. 2.5 cu. in.

The yoke on a switch or receptacle

2X cu. in. of the largest conducter in the box.

A wire passing straight through (no splices) only counts as one.

All the grounds collectively, count as one (the largest ground wire)

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...