Chris Bernhardt Posted April 5, 2007 Report Share Posted April 5, 2007 Quote:Electrical: All of the outlets are 3 hole or grounding type outlets and are not grounded. This home was built before 3 wire circuits, ones that have an EGC (equipment grounding conductor), were required. Out of convenience many homeowners replace the original 2 hole or non-grounding outlets with 3 hole outlets. This is a concern because equipment designed to rely on an EGC for safety or protection will be less safe and not protected. For personal safety having a GFCI breaker at the panel provides the best safety because once tripped the whole circuit from the panel is de-energized both hot and neutral conductors. However a GFCI does not correct the need for an EGC by equipment that relies on an EGC for protection like computers. Consider at least having any outlets that will be connected to equipment relying on an EGC (those with 3 prong plugs) rewired by an electrician and have the electrician provide GFCI protection of all the others. For even greater safety and protection have all of the outlets rewired and provided with GFCI protection. Katenize me. Chris, Oregon Quote Link to comment Share on other sites More sharing options...
Jim Katen Posted April 5, 2007 Report Share Posted April 5, 2007 Electrical: All of the outlets are 3 hole or grounding type outlets and are not grounded. This home was built before 3 wire circuits, ones that have an EGC (equipment grounding conductor), were required. Out of convenience many homeowners replace the original 2 hole or non-grounding outlets with 3 hole outlets. This is a concern because equipment designed to rely on an EGC for safety or protection will be less safe and not protected. For personal safety having a GFCI breaker at the panel provides the best safety because once tripped the whole circuit from the panel is de-energized both hot and neutral conductors. However a GFCI does not correct the need for an EGC by equipment that relies on an EGC for protection like computers. Consider at least having any outlets that will be connected to equipment relying on an EGC (those with 3 prong plugs) rewired by an electrician and have the electrician provide GFCI protection of all the others. For even greater safety and protection have all of the outlets rewired and provided with GFCI protection. Well, it makes sense to me. But I think it'd confuse the hell out of the average homebuyer. I like this little ditty: There are many ungrounded 3-slot receptacles throughout the house. These feign a level of safety that does not, in fact, exist. Ensure that all 3-slot receptacles are either properly grounded or GFCI protected for safety. Note: Never plug your computer into an ungrounded receptacle, even if itââ¬â¢s GFCI protected. Surge protectors wonââ¬â¢t work on ungrounded receptacles. -Jim Katen, Oregon Quote Link to comment Share on other sites More sharing options...
Chris Bernhardt Posted April 5, 2007 Author Report Share Posted April 5, 2007 Well, there your go. Good thing I asked. Chris, Oregon Quote Link to comment Share on other sites More sharing options...
Phillip Posted April 5, 2007 Report Share Posted April 5, 2007 Here is mine Safety Concern Old ungrounded receptacles have been replaced with modern 3 prong grounded type receptacles giving the illusion that they are grounded. The original wiring of the house did not provide for grounded receptacles. These new receptacles should be connected to ground, replaced with 2 pong outlets or GFCI receptacles where appropriate. While it is considered acceptable to leave older equipment in place that does not meet modern standards, any item you replace must meet them. Any appliance that has a three-prong plug must be provided with a grounded receptacle for safety reasons. Quote Link to comment Share on other sites More sharing options...
allspec33351 Posted April 5, 2007 Report Share Posted April 5, 2007 All of your 3 pronged receptacles (outlets) are not grounded. Have electrician ground them or replace with two pronged receptacles. It is dangerous to leave this uncorrected and could lead to death. Captain Quote Link to comment Share on other sites More sharing options...
carle3 Posted April 6, 2007 Report Share Posted April 6, 2007 This is similar how my discussion went with my fellow inspectors over the course of a couple beers. I found it amazing how widely our opinions varied. From "hey your electronics could be at risk to the death and destruction opinion. After seeing the S trap thread I think the next beer and round table discussion I am going to drop that topic on the table. I think in the end these discussions are good because we do need some commonality in our reports. In the end it is important because the client is not educated enough to know what is accurate and what may be inspector babble from the good ole\d inspector training schools. Quote Link to comment Share on other sites More sharing options...