electric Furnace Sizing


MTL_Inspet_Man

Recommended Posts

Did an inspection today

2000 sq. ft. home

Electric furnace ICG 1982

18Kw on 125 amp breaker

Furnace Rated 100Amp

What is the conversion for Kw to Btu?

So I can determine Btu output and find that furnace is or no sufficiently sized

thx

Figure 3412 BTU/hr is about the same as 1 Kw/hr.

Electric furnaces down here in the states usually come in 5kw increments. I've never heard of an 18kw furnace.

- Jim Katen, Oregon

Link to comment
Share on other sites

Do you just use BTUs to determine if the furnace is sized correctly? Is there any consideration given to ceiling and wall insulation and to window U-factors and SHG? Do you do a blower door and duct blaster to check the leakage? I do not think using BTUs alone will give use an accurate answer. Use Manual J to properly size a ubit.

Link to comment
Share on other sites