PVC trap enclosed in concrete


randynavarro

Recommended Posts

For those interested, I found it.

IRC P2603.3

I've got my IRC on two different computers so I can't copy/paste easily on to this post.

"Pipes pasing through concrete. . . shall be protected against external corrosion by a protective sheathing or wrapping or other means that will withstand any reacation from lime and acid of concrete, cinder or other corrosive material."

Link to comment
Share on other sites

The slip joint waste and overflow looks like it has the bottom slip nut connection buried in the concrete, which is not allowed. (IPC 405.8)

The plastic passing through the concrete is a different issue. Some municipalities around here (D/FW area) require it to be wrapped in 5 mil plastic. In my experience I have not seen a piece of PVC or ABS that has reacted with concrete in any meaningful way, so I would consider that a minor point (if not irrelevant). The code commentary for IPC section 305.1 specifically mentions brass, copper, cast iron and steel as the only materials that are required to be protected from corrosion.

And make sure of the code the area uses. IRC (and IPC) versus UPC are very different in many important details (venting especially).

Link to comment
Share on other sites

And make sure of the code the area uses. IRC (and IPC) versus UPC are very different in many important details (venting especially).

Yes, I don't have any IPC resources in my library.

I'm not up to speed on the plastic-concrete contact issue. Brandon mentioned it wouldn't be an issue - no bad stuff in the concrete to attack the plastic.

It makes perfect sense to sleeve the piping, though. Movement / shrinkage of the concrete can wreak some havoc on pipes. Additionally, if a pipe is trapped in the concrete, the pipe's expansion and contraction can cause damage (to the pipe itself.)

Someone can set me straight if these reasons aren't why sleeving or isolation the pipe is required.

Link to comment
Share on other sites

I'm not up to speed on the plastic-concrete contact issue. Brandon mentioned it wouldn't be an issue - no bad stuff in the concrete to attack the plastic.

It's not an issue. I still like to see things sleeved because the house and the fill around the house don't always move at the same rate. A sleeve allows a little slip and helps prevent kinks or shears.

Link to comment
Share on other sites

Out of curiosity, I would like to ask how many people here have seen a pipe embedded in concrete that has been broken by foundational movement? I'm not counting when a foundation has been repaired and the repair caused residual breakage.

I've seen breaks from foundation fixes, roots in the yard, settling under the house on horizontal cast iron pipe joints, copper water lines in contact with the concrete corroded away but never pvc breaking or even cracking because of settling issues. This being said, I know I haven't seen everything out there.[:)]

Link to comment
Share on other sites

Out of curiosity, I would like to ask how many people here have seen a pipe embedded in concrete that has been broken by foundational movement? I'm not counting when a foundation has been repaired and the repair caused residual breakage.

I guess that's why I'm an advocate for sleeves. I've seen two copper water services kinked to the point where volume was an issue. Both passed through cmu walls and were grouted in place.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...