The photos below are of an exhaust system for a 1966 oil-fired furnace
Of course I wrote it up as a suspected oil-burner adjustment problem and called for the works.
I'm curious what is causing this peculiar type of residue and leaching. I know that H20 is a big biproduct of natural gas exhaust, but I wasn't as sure about fuel oil. Could it be a restricted flue?
Thought maybe someone will recognize this specific condition.
Thanks in advance.
42.19 KB
56 KB
I see that frequently, although more so on gas units than oil-fired.
It's the corrosive particulate from the metal flue oozing down and out of the seams 'cuz the exhaust is condensing too quickly.
If you do a bit of searching on this site, there have been at least a few discussions.
  Quote
H20 is a byproduct of combustion. You ever notice water dripping out of vehicle exhaust pipes?
You probably don't see it there as often as with gas because oil burners operate at a lower combustion efficiency. I see it quite often as I inspect a lot of buildings that have been converted to oil heat when the chimney was designed and sized for coal. Coal heat kept chimneys warmer and didn't have rapid on/off cycles. With oil, these chimney flues are now at a lower temp., resulting in significant (and very acidic) condensation.
Was the flue oversized? unlined? Chimney on the exterior of the building?
It's 8" diameter with a few feet of horizontal before hooking up with a masonry chimney (9 X 13) so I suppose it cools down darn fast. It was just odd for an oil-burner around here - especially at every joint and hole. And, yes, Bill, the chimney is on the rear exterior wall - the NW wall, at that - never sees the sun.