My son-in-law in is the process of installing a generator backup system at their home. There are (4) multi-wire circuits that he plans on moving over to the transfer panel. When he went for the permit today he was told that he will need to use "handle ties" on the breakers of these multi-wire circuits. I have never been aware of the need for "handle ties" on multi-wire circuits other than on the disposal/dishwasher outlet. They are located in WA state, in a suburb of Seattle, anyone else ever run into something like this?

Link to comment
Share on other sites

210.4 Multiwire Branch Circuits.

(A) General. Branch circuits recognized by this article

shall be permitted as multiwire circuits. A multiwire circuit

shall be permitted to be considered as multiple circuits. All

conductors of a multiwire branch circuit shall originate

from the same panelboard or similar distribution equip-

ment.

FPN: A 3-phase, 4-wire, wye-connected power system

used to supply power to nonlinear loads may necessitate

that the power system design allow for the possibility of

high harmonic currents on the neutral conductor.

(B) Disconnecting Means. Each multiwire branch circuit

shall be provided with a means that will simultaneously

disconnect all ungrounded conductors at the point where

the branch circuit originates.

© Line-to-Neutral Loads. Multiwire branch circuits

shall supply only line-to-neutral loads.

Exception No. 1: A multiwire branch circuit that supplies

only one utilization equipment.

Exception No. 2: Where all ungrounded conductors of the

multiwire branch circuit are opened simultaneously by the

branch-circuit overcurrent device.

FPN: See 300.13(B) for continuity of grounded conductor

on multiwire circuits.

(D) Grouping. The ungrounded and grounded conductors

of each multiwire branch circuit shall be grouped by wire

ties or similar means in at least one location within the

panelboard or other point of origination.

Exception: The requirement for grouping shall not apply if

the circuit enters from a cable or raceway unique to the

circuit that makes the grouping obvious.

Link to comment
Share on other sites

(B) Disconnecting Means. Each multiwire branch circuit

shall be provided with a means that will simultaneously

disconnect all ungrounded conductors at the point where

the branch circuit originates.

Brandon, what version of the NEC is the para from? As almost all of the circuits in their existing panel are multi-wire circuits and none of the breakers have "handle ties".

Link to comment
Share on other sites

  • 3 weeks later...

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...