Marc Posted June 23, 2019 Report Share Posted June 23, 2019 I've got this water heater installed in a sheet metal lean-to on the side of today's house. The gas appliance connector starts just inside the crawl, exits the crawl in plain view, then goes through an opening into the lean-to. Everything on this new heater install looks DIY. Is this appliance connector ok? Quote Link to comment Share on other sites More sharing options...
Bill Kibbel Posted June 23, 2019 Report Share Posted June 23, 2019 I would say no. A connector shouldn't pass through a wall, partition or housing. Quote Link to comment Share on other sites More sharing options...
Jim Katen Posted June 23, 2019 Report Share Posted June 23, 2019 And the appliance shutoff valve has to be upstream of the connector AND in the same room as the appliance. . . Quote Link to comment Share on other sites More sharing options...
Marc Posted June 23, 2019 Author Report Share Posted June 23, 2019 Great! Thanks Guys. Quote Link to comment Share on other sites More sharing options...