I checked out a new house last week that had a panel containing neutrals and grounds mixed--not double-tapped--together on the two side buses. I phoned the electrical inspection dept. and was told that they only require the grounds and neutrals to be on separate buses if the main breaker is located away from the panel; like on the exterior of the house, near the meter. The logic of this escapes me.

Link to comment
Share on other sites

"...they only require the grounds and neutrals to be on separate buses if the main breaker is located away from the panel"

If the main breaker was part of this panel, then it is the service equipment and the neutrals would not be isolated.

If this panel was separate from the main breaker, then it is after the service equipment and the grounds and neutrals would need to be separated.