Danny Pritchard Posted April 14, 2006 Report Share Posted April 14, 2006 Saw a pool today that had low voltage yard lamps within 5' of the pool.NEC Article 411.4 says they must be at least 10'away unless permitted by Article 680. The lights were plugged into a GFI protected outlet.I went thru 680 and did not see anything to dispute the 10' rule.My thought is since it is on a GFI it is acceptable.Would this be correct? Quote Link to comment Share on other sites More sharing options...
BADAIR Posted April 17, 2006 Report Share Posted April 17, 2006 Danny, I'd have to defer this one to the AHJ just to be safe. Regional opinion will most likely be different. Codes interpretation is a tricky business and there are opinions galore, just look at these boards. Mine wouldn't matter in Jacksonville, FL. Quote Link to comment Share on other sites More sharing options...
hausdok Posted April 17, 2006 Report Share Posted April 17, 2006 Hi, Pools and I are strangers. I think I've had only 5 - 6 homes with pools in 10 years. That said, I think it has to be at least 5ft and on a GFCI so I think you're OK. Now watch Norm or Mark come on here and nuke the guy from the opposite corner of the country. [:-scared] OT - OF!!! M. Quote Link to comment Share on other sites More sharing options...
Norm Posted April 17, 2006 Report Share Posted April 17, 2006 NEC Article 680.22(B)(1),(3),(4), & (5) spells it out. The NEC doesn't differentiate between low and high voltage Luminaires(lighting fixtures), these sections state no electrical fixtures may be placed within 5' of the pool unless they are at least 5' above the maximum water level, are rigidly attached to the existing structure and protected by a GFCI circuit. NORM SAGE Quote Link to comment Share on other sites More sharing options...
Danny Pritchard Posted April 17, 2006 Author Report Share Posted April 17, 2006 THANKS! Quote Link to comment Share on other sites More sharing options...
PAbernathy Posted August 6, 2007 Report Share Posted August 6, 2007 411.4 Locations Not Permitted. Lighting systems operating at 30 volts or less shall not be installed in the locations described in 411.4(A) and 411.4(B). (A) Where concealed or extended through a building wall unless permitted in (1) or (2): (1) Installed using any of the wiring methods specified in Chapter 3 (2) Installed using wiring supplied by a listed Class 2 power source and installed in accordance with 725.52 (B) Where installed within 3.0 m (10 ft) of pools, spas, fountains, or similar locations, unless permitted by Article 680. So lets look at 680 for a sec.... Nope...enough looking as the modifications of 680 do not remove the issues of the above section. Since these lights are and will not be above the pool height to meet anything regarding 680....the 10' distance stands. Quote Link to comment Share on other sites More sharing options...
PAbernathy Posted August 6, 2007 Report Share Posted August 6, 2007 opps.......sorry...that post was like a YEAR old...my bad! Quote Link to comment Share on other sites More sharing options...
Jeff Remas Posted October 24, 2009 Report Share Posted October 24, 2009 yeah, 10'. What he said and for the same reasons. Quote Link to comment Share on other sites More sharing options...
Erby Posted October 25, 2009 Report Share Posted October 25, 2009 Some posts never die!!!! Quote Link to comment Share on other sites More sharing options...