Fireblocking in a two+ family dwelling


drw

Recommended Posts

IRC 602.8 says that "Fireblocking of cornices of a two-family dwelling is required at the line of dwelling unit separation." Would you interpret this to mean that the attic cannot be open across multi-family units? I cannot come up with a mental picture of "fireblocking of a cornice" in the context that I think of a cornice.

Link to comment
Share on other sites

R602.8 is not describing anything in an attic.

You'll want to read through section R317, "Dwelling Unit Separation". It states that a fire resistant wall assembly needs to extend to the underside of the roof sheathing (unless the ceiling assembly below the common attic meets the exception).

Link to comment
Share on other sites