Originally posted by tbird

Has anyone ever seen this. A 1978 home with two outlets installed in the kitchen countertop facing up. Besides the risk of spills and wet rags, is there anything else I should know about?

Image Insert:

2008125203851_upoutlets.jpg

38.72 KB

Violation of NEC 2008 406.4(E)

Link to comment
Share on other sites

Originally posted by mthomas1

Best to check with the local AHJ, some will not approve any type of "folding" outlet box on a kitchen counter surface. My favorite solution if you don't mind the look is a Lew Electric "floor nozzle". This one has outlets on both sides:

That's a dandy looking thing.

As for the AHJ not approving a folding outlet box, he'd be out of line. AHJs and electrical inspectors aren't supposed to substitute their opinion for the code.

In Oregon, if an inspector rejects an installation, he's got to list the code section that's the basis for his rejection. (Got to write it right on the inspection form.)

- Jim Katen, Oregon

Link to comment
Share on other sites

Originally posted by Jim Katen

In Oregon, if an inspector rejects an installation, he's got to list the code section that's the basis for his rejection. (Got to write it right on the inspection form.)

- Jim Katen, Oregon

Must be nice. We get turned down without the beneift of a code reference.

Link to comment
Share on other sites

in the case of the flip-up type, the argument is that the "face up" requirement in 406.4(e) is violated as the face of the box is pointed upwards and level with the counter-top. I've read that these:

PCS39_EE_HW.jpg

http://www.mockett.com/default.asp?ID=4&action=detail&partCode=PCS39/EE/HW

are UL listed for kitchen counters, but I don't find such a listing in the specs on the site.

Link to comment
Share on other sites

Originally posted by mthomas1

in the case of the flip-up type, the argument is that the "face up" requirement in 406.4(e) is violated as the face of the box is pointed upwards and level with the counter-top. I've read that these: . . . are UL listed for kitchen counters, but I don't find such a listing in the specs on the site.

I still say that the inspector is out of line. The NEC doesn't say peep about the direction that the box faces or whether or not it's flush to the countertop. He's substituting his opinion for the code.

- Jim Katen, Oregon

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...