PVC furnace vents


prowannabe

Recommended Posts

You're both correct, I was just wondering why the other 2 furnaces, 2 water tanks, and 2 chimney stacks all have galvanized vents but he went with pvc on this one?

Cat IV furnaces extract more heat from the exhaust which makes the exhaust much cooler when it's flowing out the pipe. This produces alot of condensate which would corrode metallic vent pipes. This is why PVC is used as it won't corrode from the condensate. The PVC is also sealed at the joints to allow the condensate to drain back down the pipe to be directed out the condensate drain. Cat IV are also commonly referred to as condensing furnaces. One thing to check on Cat IV's with PVC venting is that the horizontal runs slope slightly back towards the furnace in order to facilitate condensate drainage.

Link to comment
Share on other sites

You've got another issue there also, and it's one I see more often than not with high efficiency furnaces. I guess because they're relatively rare around here the guys who put them in don't always know what they're doing. And we all know that actually reading the instructions is too much work, what with having to tear open that little plastic bag and all. But if you look closely at your first photo, you will see that the exhaust vent is glued to the fitting on the furnace itself. This isn't right; you're supposed to use RTV silicone sealant there. The silicone allows you to pull the exhaust vent off without damaging anything if you ever need to for servicing, but it still maintains a watertight joint. It's not the end of the world as far as being a serious issue, but it's still wrong. (Well, it's wrong according to all the instructions I have seen previously. If some other manufacturer allows it I imagine someone else will correct me.)

If you run into it again, I recommend that you look around the furnace for the installation instructions. A lot of times the installer will leave them nearby. They will always have a diagram and instructions for this connection.

P.S. Being the "builders personal home" is absolutely no guarantee that things are all done correctly!

Link to comment
Share on other sites

P.S. Being the "builders personal home" is absolutely no guarantee that things are all done correctly!

It's almost always a guarantee that there's at least a few things that are done incorrectly, or more likely, a few things that just plain aren't done......yet.....

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...