EMT Running from Meter Head


Mike Lamb

Recommended Posts

How do the lighting circuit wires get into the meter box? (Assuming that they don't originate there, which would clearly be way wrong.)

230.7 prohibits branch wires in the same raceway as service conductors. So, if the light's wires get into the box by passing through the service entrance conduit or nipple, then it's clearly wrong.

The meter box, however, is not a raceway. If the lighting circuit wires enter the back of the meter box on their own, then I can't find anything specific to prohibit this. Though it does seem to defy the spirit of 230.7.

Link to comment
Share on other sites

230.7 prohibits branch wires in the same raceway as service conductors. So, if the light's wires get into the box by passing through the service entrance conduit or nipple, then it's clearly wrong.

The meter box, however, is not a raceway. If the lighting circuit wires enter the back of the meter box on their own, then I can't find anything specific to prohibit this. Though it does seem to defy the spirit of 230.7.

If it did enter the back of the meter socket, then I doubt that it would have been sealed properly. It seems like the only advantage for installing the circuit this was was to avoid drilling through the brick, so entering the back of the meter socket seems unlikely.

Bottom line-more likely wrong than not.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...