P trap directly into main stack

Recommended Posts

Had an inspection today with a p trap plumbed directly into the main stack serving the furnace/A/C condensation line. The house was slab on grade built this year. Anything wrong with the configuration? If so, any code cite would be greatly appreciated. Thanks

DSCN8604.JPG

DSCN8605.JPG

Edited by greyboy39
Punctuation error

Share this post


Link to post
Share on other sites

It's an indirect drain for non-potable, clear waste water. It's ok. The air gap prevents a sewer back up from fouling the heating/ cooling equipment. The only draw back may be if the heating/ cooling system goes unused long enough for the trap water to evaporate and lose the seal. That's a stretch though.  

Share this post


Link to post
Share on other sites
32 minutes ago, greyboy39 said:

Thanks for the clarification Chad. I initially thought it could potentially back siphon as a result of being too near the main stack. 

The air gap isn't big enough. I shouldn't have said "OK".   Honestly, I thought you were asking if it was OK because it was an indirect connection. I just spent 7 or 8 horrible minutes reading the plumbing code. It's all in chapter 8 of the IPC. I'll email it to you if you want.

 

  • Thanks 1

Share this post


Link to post
Share on other sites

"Indirect" needs an air gap.

airgap.jpg.c43dfe7ec45eef5606cff536bdc9cc3b.jpg

More and more municipalities are requiring an acid neutralizer for the condensate.

Does that P-trap have a long enough trap arm?

  • Thanks 1

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
Sign in to follow this  

×