Main panel height


MOB

Recommended Posts

Here is a first for me, Main Electrical panel is approximately 10' up from landing below. Easily accessible from side entry. I read in past posts some conflicting info. on minimum heights. From what I read 6' 7" is max. height to top of panel. Is this correct?

Click to Enlarge
tn_20103620933_Main%20Electrical%20panel.jpg

20.62 KB

Link to comment
Share on other sites

Here is a first for me, Main Electrical panel is approximately 10' up from landing below. Easily accessible from side entry. I read in past posts some conflicting info. on minimum heights. From what I read 6' 7" is max. height to top of panel. Is this correct?

Not quite. It's 6'-7" to the center of the grip of the operating handle of the highest breaker (OCPD) when in its highest position. (240.24(A))

The location in your picture is wrong.

- Jim Katen, Oregon

Link to comment
Share on other sites

I've got $100 that says it will never get changed or moved. No argument at all that it's wrong and should be reported as such but, "off the record", how much of an issue is this really? It can safely be reached, even in an emergency, by the homeowner. If it ever actually needs to be worked on, presumably a temporary safe workspace platform could be fashioned.

If this was my own home, my only real-life concern would be what the next home inspector would say when I sold it.

But...to repeat myself, it is wrong!

Link to comment
Share on other sites

While you say the panel is accessible from the side there is no way it will meet the workspace requirements in Article 110.

Which part? I can't find anything in 110 that would prohibit this.

- Jim Katen, Oregon

I doubt that many would think that 110.26 "to permit ready and safe operation and maintnance" would be meet. I would also challenge the depth of the workspace meeting the 36" depth if a ladder were used to gain access to work in the panel. I would also note that this could be argued that this is not dedicated space as required.

Link to comment
Share on other sites

I doubt that many would think that 110.26 "to permit ready and safe operation and maintnance" would be meet. I would also challenge the depth of the workspace meeting the 36" depth if a ladder were used to gain access to work in the panel. I would also note that this could be argued that this is not dedicated space as required.

I agree about the first part of 110.26 where it says that "sufficient access . . . shall be provided . . ."

But I'd reject the rest of your arguments. 110.26 is mostly about having plenty of space around the equipment. The panel in the picture has space in spades. I agree that you could construct all sorts of hypothetical scenarios that would bring 110.26 into play but there's really no reason to because you have a clear, unequivocal violation in 240.24. The problem here isn't that there isn't enough work space, it's that the equipment is too high off the floor.

Personally, I'd rather cite the section that's clear and unequivocal than try to bend another section into play with rationalizations.

- Jim Katen, Oregon

Link to comment
Share on other sites

I agree that 240.24(A) regarding the maximum height being exceeded would be the best site.

I was aware of 240.24(F), not over steps, but the OP said this was over a landing. In the Mike Holt "Changes to the NEC 2008" his analysis states that panel can be over landings. I would tend to agree. While the landing is part of the stairway it is not steps.

Link to comment
Share on other sites

I've got $100 that says it will never get changed or moved. No argument at all that it's wrong and should be reported as such but, "off the record", how much of an issue is this really? It can safely be reached, even in an emergency, by the homeowner. If it ever actually needs to be worked on, presumably a temporary safe workspace platform could be fashioned.

If this was my own home, my only real-life concern would be what the next home inspector would say when I sold it.

But...to repeat myself, it is wrong!

I agree with Richard, yes its wrong.... I would certainly note it in the report.... my biggest concern would be as Richard said: 'how much of an issue is this really? It can safely be reached, even in an emergency, by the homeowner.' ??

Jerry

Link to comment
Share on other sites

I've got $100 that says it will never get changed or moved. No argument at all that it's wrong and should be reported as such but, "off the record", how much of an issue is this really? It can safely be reached, even in an emergency, by the homeowner. If it ever actually needs to be worked on, presumably a temporary safe workspace platform could be fashioned.

If this was my own home, my only real-life concern would be what the next home inspector would say when I sold it.

But...to repeat myself, it is wrong!

I agree with Richard, yes its wrong.... I would certainly note it in the report.... my biggest concern would be as Richard said: 'how much of an issue is this really? It can safely be reached, even in an emergency, by the homeowner.' ??

Jerry

It's not an issue till something goes wrong. Then it's a big issue.

- Jim Katen, Oregon

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...