Installing a 100 amp breaker in a 200 amp panel

Recommended Posts

This panel is using a copper 1 AWG at a 200 amp main disconnect. The service entrance pipe is going to be too small for 3/0.  This house does not need a 200 amp main. Will it be a problem to put 100 amp main into this 200 amp panel slot?

P7110013a.JPG

Share this post


Link to post
Share on other sites

You'll need to ask your local (Challenger) electrical wholesaler if a 100 will fit in place of a 200 in that particular model of panel.  I think there's a decent chance of finding a 175 or less that will work. 1/0 is ok on a 175 A service.

I'd do a load analysis first to find out just how big a service you'll need.  The NEC has instructions for doing that.  That's more up a sparky's alley than an HI's though.

Edited by Marc

Share this post


Link to post
Share on other sites

Yes, 1/0 AWG is one size larger than 1 AWG.

Dang, now I see my mistake.  OK, a 150 A breaker or smaller will work once you confirm the actual load with a load analysis.

Sorry.