House with a detached barn. Inside the main electrical panelboard, the 240-volt wiring feeds for the barn exit the main panelboard back-through the raceway that contains the main service entrance cables, then some how/some way out to the barn. That's a Bozo No-No, isn't it (using the SEC raceway for lower branch circuit wiring)?

Link to comment
Share on other sites

again.. "But why.. ??" :) Knowing 'why' is more important that 'chapter and verse'..

What Marc said. The fused or downstream feeders are at risk of being energized by the service conductors.

In Canada, it is not permitted to have branch circuit wiring anywhere near the service conductors. In a combination breaker panel, a divider is installed to keep the service conductors and the main breaker separate from the branch circuits. Only an amateur will feed a new branch circuit in past the service conductors, which we find now and then when buddy has installed a hot tub.

Jerry, so how was the foundation? Or did you post that info already in the Roof forum?

Link to comment
Share on other sites

again.. "But why.. ??" :) Knowing 'why' is more important that 'chapter and verse'..

What Marc said. Plus, putting the two together creates the possibility for a fault to cross over from the unprotected service wires to the feeders.

I don't know why we don't keep them completely separate, like Canada does.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...