Plumbing Vent through wall


Mike Lamb

Recommended Posts

I think it depends on the code.

IRC = yes

UPC = no

Chicago = ???

IRC

P3103.6 Extension through the wall.

Vent terminals extending through the wall shall terminate not less than 10 feet (3048 mm) from the lot line and 10 feet (3048 mm) above the highest adjacent grade within 10 feet (3048 mm) horizontally of the vent terminal. Vent terminals shall not terminate under the overhang of a structure with soffit vents. Side wall vent terminals shall be protected to prevent birds or rodents from entering or blocking the vent opening.

Link to comment
Share on other sites

Download one of those documents to get an idea of what it's like trying to decipher City of Chicago codes. Fuggedaboudit.....

What you want is HERE....

Click on the "More" button.... Go to division 29, where I found out I was wrong.

"18-29-904.6 Extension through the wall.

Vent terminals extending through the wall shall terminate a minimum of 12 feet (3.66 m) from the lot line and 12 feet (3.66 m) above average ground level. Vent terminals shall not terminate under the overhang of a structure with soffit vents. Side wall vent terminals shall be protected to prevent birds or rodents from entering or blocking the vent opening."

There it is, almost identical to the IRC except for the 12' vs. 10' thing, and I've been told by every union shop in Chicago that you can't do it. Just goes to show......

Just because it's in the book doesn't mean squat. It's what the union guy says whenever they say it. I alternate between hating and loving this city.

It's been a while since I've waded into that mess.....there's a few changes...

Link to comment
Share on other sites

If it's copper pipe, I advise them to keep it painted to look like plastic. [:)]

Freezing should be no problem because the pipes should drain.

Even so, some old timer thought they might freeze, so he built a box around his outdoor drainpipes and filled that with sawdust. Carpenter ants found that to be to their liking and raised 100 generations of ants there, no doubt. [:)]

Link to comment
Share on other sites

Actually, 'freezing' is a concern.

I have seen a 1 1/2" vent pipe that came thru and extended about 2 feet above the roof. The entire interior of the pipe was 'frosted' over. That's why running a vent on the exterior wall is a no no in cold climate areas.

Link to comment
Share on other sites

I've seen hard winters where multifamily buildings with 6" vents are almost closed, and 4" is completely closed by frost. 3" is the bare minimum.

Admittedly, frost closure is pretty rare (I've only seen it a few times in my entire career, and it's always early morning/dawn, but if one thinks there needs to be an open vent 24/7/365/infinity, it better be a big vent coming out the roofline.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...