3 hours ago, Denray said:

Have a new 95+ Rheem heater. 
When the power is out, and on a generator, only the fan will come on, but burners won't light. My old 80% would light up no problem. 
Any ideas?

I assume this is a gas-fueled furnace. Grounding and correct polarity of the incoming power is vital in order for ignition to function. The ignition card will detect if the polarity is incorrect and fail the ignition every time.

Link to comment
Share on other sites

If this is a portable generator with an extension cord, the grounding shouldn't matter as long as you're using an extension cord with a grounding wire and intact connections at each end. 

If this is a permanent setup with a transfer switch, the generator should have its own grounding connection to the earth, just as you'd have at the power company's service point. 

Grounding problems to a furnace usually result in the flame sensor not working properly, in which case the unit would at least try to start up, but then shut down when it couldn't prove the flame. If the flame doesn't even try to start, something else it probably wrong, but I couldn't say what. Try calling Rheem. 

Link to comment
Share on other sites

Rheem sent me to an online that was going to cost. Which I didn't try.

Been told it's a polarity issue that somehow relates to grounding. Very new 95+ and full of computerish hardware. I have no warranty on this rig, but I think it's not it's fault. Heater installer has large output generator at his house wired into service panel for his same as mine furnace. Mine runs fine on house electric.

 

Link to comment
Share on other sites

1 hour ago, Denray said:

Rheem sent me to an online that was going to cost. Which I didn't try.

Been told it's a polarity issue that somehow relates to grounding. Very new 95+ and full of computerish hardware. I have no warranty on this rig, but I think it's not it's fault. Heater installer has large output generator at his house wired into service panel for his same as mine furnace. Mine runs fine on house electric.

 

I spend a lot more time on recreational vehicle FB pages than I do here. Lots of appliances and power filtering devices will give trouble if your power plant isn't grounded. It's all the new electronics.

Check if your power plant is already grounded. If it isn't, you need to do it somewhere on your premises wiring. Just be absolutely sure that it isn't grounded twice.

Link to comment
Share on other sites

If it's a portable generator that only uses extension cords, then there is no reason to make a connection to the earth. The frame of the generator is the "ground." As long as the extension cord has an intact equipment grounding conductor and as long as the grounding wire's socket and pin are it good condition, then the furnace will see this as grounded. 

Also, a generator is not an inverter and the furnace should not see it as one. 

Is this how your system is set up, or are you using a transfer switch? 

Link to comment
Share on other sites

5 hours ago, Denray said:

This is how it is advertised by Honda

Honda EU1000i - 900 Watt Portable Inverter Generator w/ CO-MINDER™ (CARB)

Extension cord connection only. My furnace installer friend has his furnace, same as mine, connected to a standard generator, when our power goes out.

That's an excellent choice of generator. I'm saving for the EU 3000 myself for my travel trailer.

I suspect most good generators don't automatically ground the neutral because it isn't known if the RV, or whatever you connect it to, is also grounded. Two separate grounding points introduce neutral currents into the ground wire, which is to be avoided. Look at the schematic that came with the generator. If it doesn't show a bonding point between neutral and ground, ground it yourself and see if the furnace works.

Edited by Marc
Link to comment
Share on other sites

According to the instructions ( https://www.electricgeneratorsdirect.com/manuals/Honda EU1000i Manual 2013.pdf  page 38), the equipment grounding wires are bonded to the frame of the generator but not to the neutral. This makes little sense  because the EGCs will never clear a fault that way. This also explains why your furnace won't work while connected to it. The instructions don't mention it, but there should be a bonding strap that bonds the neutral to the EGC. I'd make that connection and try again. 

Link to comment
Share on other sites

"Then just try bonding the grounding terminal to the neutral at the generator - even temporarily as a troubleshooting measure".
So, we did that and the fan turned on, but then there was this click click noise? And then the burners lit up. And a little later there was warm air coming out our vents. 
Color us happy!
Thanks again for your help on this. 
Pulled off the panel holding the outlets on the generator and right on the back side there was a hole to push the jumper in and a screw right next to it to complete the bonding. Piece of cake.

PXL_20230126_213015456.NIGHT.jpg

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...