Is the unit chassis bonded to ground?

I can't say 100%. I know the green grounding wire in that 3rd pic. runs out of the disconnect box, thru the flex conduit (plastic - I forget the name of it right now), and into the A/C housing. I'm assuming it's bonded inside the A/C housing. . .

Click to Enlarge
tn_20091210191155_DSC05728.jpg

78.04 KB

Does anyone check wiring connections inside the A/C housing?

Link to comment
Share on other sites

Yup! Seems like "someone" used the EMT as an equipment grounding conductor. Ok for the most part, however, notice the paint under the connector in the main panel. Too easy to make it a better, safer installation by running a EG conductor back to the main panel's grounding bus. Plus, not a good idea to use conduit as an EG when there are concentric/ecentric K.O.s. Believe it violates NEC; 90% sure.

Link to comment
Share on other sites

Yup! Seems like "someone" used the EMT as an equipment grounding conductor. Ok for the most part, however, notice the paint under the connector in the main panel. Too easy to make it a better, safer installation by running a EG conductor back to the main panel's grounding bus. Plus, not a good idea to use conduit as an EG when there are concentric/ecentric K.O.s. Believe it violates NEC; 90% sure.

You can't rely on the knockout for grounding for circuits that are over 250v or for the bonding of the service. As far as I know, the knockouts aren't a problem on branch circuit equipment grounds.

You make a good point about the paint. If you're using the EMT as the equipment ground, and if the box is painted, then you're supposed to remove the paint at the locknut to ensure a good connection.

- Jim Katen, Oregon

Link to comment
Share on other sites

"You make a good point about the paint. If you're using the EMT as the equipment ground, and if the box is painted, then you're supposed to remove the paint at the locknut to ensure a good connection."

So how common is it to see the paint removed? And shouldn't the same prep be at the accessory ground bus in the disconnect (or any accessory bus for that matter)?

Tom

Link to comment
Share on other sites

And shouldn't the same prep be at the accessory ground bus in the disconnect (or any accessory bus for that matter)?Tom

I would think because the equipment is assembled at the factory, that those bond and connection points are ok.

It's when field modifications are made that the paint may become a problem.

I could be wrong though.

Link to comment
Share on other sites

. . . So how common is it to see the paint removed? And shouldn't the same prep be at the accessory ground bus in the disconnect (or any accessory bus for that matter)?

Uncommon.

At the accessory grounding terminal, I believe that the electrica connection is made via the mounting screws.

- Jim Katen, Oregon

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...