twisted neutrals


Jerry Lozier

Recommended Posts

Never seen grounded conductors done this way... I call them out when there are 2 or more or combined with a ground under one lug on bar. However there is no way one could come loose and both are same gauge 12awg... any problem here??

Yes there are 2 grounds at lug above with different gauges, probably not best practice.

Download Attachment: icon_photo.gif P5250051.JPG

82.18 KB

Link to comment
Share on other sites

Never seen grounded conductors done this way... I call them out when there are 2 or more or combined with a ground under one lug on bar. However there is no way one could come loose and both are same gauge 12awg... any problem here??

Yes there are 2 grounds at lug above with different gauges, probably not best practice.

Twisted or not, the lugs aren't listed to hold more than one neutral.

The twisting will make it slightly more difficult to isolate a circuit during furture trouble shooting.

Nothing about the twisting method is "better" than simply sticking the two wires under the lug.

- Jim Katen, Oregon

Link to comment
Share on other sites

Never seen grounded conductors done this way... I call them out when there are 2 or more or combined with a ground under one lug on bar. However there is no way one could come loose and both are same gauge 12awg... any problem here??

Yes there are 2 grounds at lug above with different gauges, probably not best practice.

Twisted or not, the lugs aren't listed to hold more than one neutral.

The twisting will make it slightly more difficult to isolate a circuit during furture trouble shooting.

Nothing about the twisting method is "better" than simply sticking the two wires under the lug.

- Jim Katen, Oregon

thanks Jim, good point, had not thought about the isolation challenge.... you are an excellant source for consistantly good info.... so that brings up multiple grounds under lug rated for one wire, or is lug rated only for (no more than one neutral because it cares current?)

Link to comment
Share on other sites

. . . so that brings up multiple grounds under lug rated for one wire, or is lug rated only for (no more than one neutral because it cares current?)

The lugs will typically be rated for two or three grounding wires (depending on the size of the wires), but only one "grounded" (neutral) wire because, as you say, it carries current. The grounding wires only have to carry current for a split second.

You'll find the lugs' limitations printed on the panel schematic.

- Jim Katen, Oregon

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...