gfi breaker issue

Recommended Posts

Looking for some input. I have a customer who has old bx wiring(2 wire) that feeds the countertop of the kitchen. There is no gfi protection and with that I was hoping to install gfi breakers instead of individual gfi's. The customer has special wall plates that can't be replaced to fit if we do individual gfi's. The issue is that when the neutral is connected to the breaker and the factory neutral is connected to the neutral/grnd bar it automatically trips when power is restored. Is this because the bx is bonded to the cabinet and because the bonding screw is installed through the ground bar to the cabinet, its tripping because the shared connection between ground and neutral?

Share this post


Link to post
Share on other sites

No, it shouldn't.  Maybe the GFCI breaker is simply doing it's job.  Maybe there is leakage.  Takes only about 5/1000 of an amp to trip it.

Pull out the 1st receptacle in the string.  Leave it connected but, at that point, disconnect the rest of the string then try again.  See if it trips.

If you're removing power from the bus, reset the GFCI breaker after the bus is live.

Edited by Marc

Share this post


Link to post
Share on other sites

Tim, that circuit is most likely sharing a neutral with another circuit.....very common in older wiring installations. The imbalance of neutral current in the two circuits will cause the GFCI to trip, or as Marc said, there could actually be a ground fault on the circuit. If it is sharing a neutral with another circuit, your customer may just have to lose their affection for the old plates. Then you can use GFCI receptacles for the countertop receptacles, as long as you don't use the load terminals for other downstream outlets/receptacles.

Edited by mtwitty
  • Like 1

Share this post


Link to post
Share on other sites
16 hours ago, mtwitty said:

If it is sharing a neutral with another circuit, your customer may just have to lose their affection for the old plates.

I see a 3-d printer in their future . . . 

Share this post


Link to post
Share on other sites
On 2/7/2020 at 9:02 AM, mtwitty said:

Tim, that circuit is most likely sharing a neutral with another circuit.....very common in older wiring installations. The imbalance of neutral current in the two circuits will cause the GFCI to trip, or as Marc said, there could actually be a ground fault on the circuit. If it is sharing a neutral with another circuit, your customer may just have to lose their affection for the old plates. Then you can use GFCI receptacles for the countertop receptacles, as long as you don't use the load terminals for other downstream outlets/receptacles.

Thank you.

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Sign in to follow this  

×
×
  • Create New...