Arc Flash


MPdesign

Recommended Posts

I thought that I should pass this along in case anyone was interested.

This is what my research has shown:

In an existing building, the labeling (therefore triggering a study) must be completed if the equipment is going to be worked on hot.

So if you are in a commercial facility and you pass people working on the hot panels while you are there, and it is not labeled, then you should mention it in the report. This may be true in residential as well - I am not sure.

Will this happen? Probably not, but it is a requirement of NFPA 70E for those circumstances.

Link to comment
Share on other sites

I thought that I should pass this along in case anyone was interested.

This is what my research has shown:

In an existing building, the labeling (therefore triggering a study) must be completed if the equipment is going to be worked on hot.

So if you are in a commercial facility and you pass people working on the hot panels while you are there, and it is not labeled, then you should mention it in the report. This may be true in residential as well - I am not sure.

Will this happen? Probably not, but it is a requirement of NFPA 70E for those circumstances.

Labeled how?

Marc

Link to comment
Share on other sites

I thought that I should pass this along in case anyone was interested.

This is what my research has shown:

In an existing building, the labeling (therefore triggering a study) must be completed if the equipment is going to be worked on hot.

So if you are in a commercial facility and you pass people working on the hot panels while you are there, and it is not labeled, then you should mention it in the report. This may be true in residential as well - I am not sure.

Will this happen? Probably not, but it is a requirement of NFPA 70E for those circumstances.

Are you inspecting the building or are you the employer or facilities manager?

NFPA 70E is the guidelines for worker safety developed for OSHA - it's not for any building codes. If you are going to report on signs for approach boundaries, you had better have done arc flash and shock hazard analysis to determine where signs are needed. Are you going to report on all of the other OSHA requirements for worker safety too?

Link to comment
Share on other sites

I am inspecting the building not the practices of the building. So, yes - this is really out of our realm.

I originally asked this topic because I had seen it called out on another inspector's report as being required by code. It appears this was not really needed because he had no other explanation other than "complete arc flash study as required by code".

I hope that this post helps others who may hear about this subject and need more info to clear it up.

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

×
×
  • Create New...