Marc Posted June 9, 2019 Report Share Posted June 9, 2019 (edited) Ok. Another question: does the frosting in cool mode go all the way back to the indoor section? Or does it begin and end within the outdoor section? Edited June 9, 2019 by Marc Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted June 9, 2019 Author Report Share Posted June 9, 2019 The lines are currently concealed at the evap end. However the visible portions of high line on the exterior of the condenser do frost up. And that frosting continues up the line into the jacket. But I can’t see very far up the jacket. Quote Link to comment Share on other sites More sharing options...
Marc Posted June 9, 2019 Report Share Posted June 9, 2019 (edited) Looks like a classic case of low refrigerant charge. This assumes that the air filter and evap coil are both clean, since the unit is new, that the evap fan is working and that air is moving through the evap coil and finally, that the indoor temps are 70 or higher. The frost begins at the evap coil, becoming ice that eventually completely encapsulates the coil, stopping all air flow. Thereafter, frost makes it way up the vapor line all the way to the outdoor section. There's a chance that there is no refrigerant leak, that it's been making ice since the installation but the off cycles have been long enough to melt the ice...until now. Edited June 9, 2019 by Marc Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted June 9, 2019 Author Report Share Posted June 9, 2019 Then wouldn’t that mean the low pressure line would be frosting? Because it’s the high pressure side returning from the evap that’s frosting, not the low side. Quote Link to comment Share on other sites More sharing options...
Marc Posted June 9, 2019 Report Share Posted June 9, 2019 (edited) I think the story on those 2 coiled tubings and the bubble thingy are a capillary tube in parallel with a check valve. The check valve opens in cool mode so that the capillary tube in the outdoor section is bypassed, allowing the capillary tube, or expansion valve, in the indoor section instead, to drop the pressure and start the liquid evaporating. In heat mode, the check valve closes, forcing the returning liquid to go through the capillary coil in the outdoor section, causing the returning liquid to evaporate in the outdoor coil so it can collect heat. The indoor capillary tube likely has its own check valve that opens in heat mode. Perhaps there's a problem with the check valve (bubble thingy) not opening as much as it should, making it an...ahem...obstruction of sorts. Obviously, I haven't been of any help. Edited June 9, 2019 by Marc Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted June 9, 2019 Author Report Share Posted June 9, 2019 Marc, you have been a great help. Double checking my thought process is important. Tomorrow I will call the Mr Cool tech line. I’ll let you know how that discussion goes. Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted June 10, 2019 Author Report Share Posted June 10, 2019 Tech guy at Mr Cool is suspicious of improper refrigerant charge, either high or low. I ordered my own manifold gauge set. When it gets here and I get the numbers, I’ll post back. He wants to see 120-150psi in 80 degree ambient. Quote Link to comment Share on other sites More sharing options...
Marc Posted June 10, 2019 Report Share Posted June 10, 2019 I use 115 to 120 for vapor line, checked when indoor ambient is at target temperature. Liquid line depends on outdoor temps. What kind of torch do you have for brazing? Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted June 11, 2019 Author Report Share Posted June 11, 2019 I have a MAP torch. Is that good enough? Quote Link to comment Share on other sites More sharing options...
Marc Posted June 11, 2019 Report Share Posted June 11, 2019 Try it on some scrap pieces of copper. Oxy/Acytl is all I've ever used for brazing with silver solder. Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted June 11, 2019 Author Report Share Posted June 11, 2019 I’m not yet convinced that brazing will be needed. We will see what happens when the tools get here. Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted June 12, 2019 Author Report Share Posted June 12, 2019 When refrigerant is recovered prior to the proper recharging of a system, can that recovered portion be put back in? Obviously you would weigh it. Then add the remaining weight to top off the system? Quote Link to comment Share on other sites More sharing options...
Chad Fabry Posted June 12, 2019 Report Share Posted June 12, 2019 1 hour ago, John Dirks Jr said: When refrigerant is recovered prior to the proper recharging of a system, can that recovered portion be put back in? Obviously you would weigh it. Then add the remaining weight to top off the system? One recovers refrigerant to a recovery tank, not to the virgin tank. When I was in the automotive business, I never used the recovered product because there was no assurance of purity. I sold it to a recycler. Unless you know for sure what's in your guy's tank, I'd be slow to ask for recovered product. Quote Link to comment Share on other sites More sharing options...
Marc Posted June 12, 2019 Report Share Posted June 12, 2019 (edited) Refrigerant can be re-used in the same system as long as the compressor hasn't burned out. You'd need a recovery tank to remove the original charge. Like Chad said, the virgin tanks have a check valve in the neck, can't put the toothpaste back in the tube. I've never charged an AC system by weight before, except for my truck's AC, but you could charge your mini-split that way. You'd need a scale on par with the weight of your tank. A bathroom scale would be too crude. I used a mechanical scale for my truck: a 10' long 2X10 with a pivot in the middle, the recovery tank sitting on one end and a dead weight with one can of Hunt's Steam-Peeled Tomatoes, whose weight matched the stated refrigerant charge for my AC, on the other. When perfectly balanced, remove the tomatoes and charge until the scale balances out again. Distance from tomatoes to pivot has to equal distance from tank to pivot. It's very precise...and fun. Edited June 12, 2019 by Marc Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted June 12, 2019 Author Report Share Posted June 12, 2019 72 degree ambient. System hasn’t been run in two days. Vapor side reading 150psi at idle (not running) So, this indicates there has not been a loss of refrigerant. Am I correct? Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted June 12, 2019 Author Report Share Posted June 12, 2019 Wait. When running it drops to 35psi. Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted June 13, 2019 Author Report Share Posted June 13, 2019 13 hours ago, Marc said: Refrigerant can be re-used in the same system as long as the compressor hasn't burned out. You'd need a recovery tank to remove the original charge. Like Chad said, the virgin tanks have a check valve in the neck, can't put the toothpaste back in the tube. I've never charged an AC system by weight before, except for my truck's AC, but you could charge your mini-split that way. You'd need a scale on par with the weight of your tank. A bathroom scale would be too crude. I used a mechanical scale for my truck: a 10' long 2X10 with a pivot in the middle, the recovery tank sitting on one end and a dead weight with one can of Hunt's Steam-Peeled Tomatoes, whose weight matched the stated refrigerant charge for my AC, on the other. When perfectly balanced, remove the tomatoes and charge until the scale balances out again. Distance from tomatoes to pivot has to equal distance from tank to pivot. It's very precise...and fun. I have an electronic postal scale with 30lb max capacity. It measures in increments as low as 1/10 ounce. It also does grams. This type of scales would be adequate wouldn't you think? Quote Link to comment Share on other sites More sharing options...
Marc Posted June 13, 2019 Report Share Posted June 13, 2019 (edited) The photo, when the unit isn't running, indicates 150 psi which, for 410A corresponds to a saturation temperature of 52 degrees (look at the R410A temperature saturation scale, the outer blue one). If I assume that both indoor and outdoor temps are at 72 degrees, this means there is no longer any liquid refrigerant left in the system. When there is at least some liquid and some vapor in the system, no matter how little or how much, pressure will be at saturation. So your system is all vapor, unless its 52 degrees outside. That would mean it has lost most of its refrigerant, I'd guess about 90% at least. That's a really fast leak and, in my book, a good sign because it'll make it easier to find. Edited June 13, 2019 by Marc Quote Link to comment Share on other sites More sharing options...
Marc Posted June 13, 2019 Report Share Posted June 13, 2019 I would not run this system anymore until its fixed. When refrigerant is low, oil circulation, which prevents the compressor from overheating and failure, suffers. Quote Link to comment Share on other sites More sharing options...
Marc Posted June 13, 2019 Report Share Posted June 13, 2019 (edited) 1 hour ago, John Dirks Jr said: I have an electronic postal scale with 30lb max capacity. It measures in increments as low as 1/10 ounce. It also does grams. This type of scales would be adequate wouldn't you think? That would be ideal if you bought an R410A under 24 lbs. A 30lb weighs 6 lbs empty, 36 lbs when new. Edited June 13, 2019 by Marc Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted June 13, 2019 Author Report Share Posted June 13, 2019 Thanks Marc, what would be a normal “resting” pressure at 75 degrees ambient? Ball park Quote Link to comment Share on other sites More sharing options...
Marc Posted June 13, 2019 Report Share Posted June 13, 2019 (edited) 220. Its on your gauges. Edited June 13, 2019 by Marc Quote Link to comment Share on other sites More sharing options...
Jim Katen Posted June 14, 2019 Report Share Posted June 14, 2019 How do you plan to buy the refrigerant without a license? Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted June 14, 2019 Author Report Share Posted June 14, 2019 Jim, An acquaintance of mine is EPA certified to handle refrigerants and has begun helping me service this system. We discovered a poorly connected fitting which has been fixed. Although the system had leaked down, any remainder was evacuated, the system vacuumed and recharged by weight according to the information on the data plate. The repaired fitting was tested and verified leak free. The system is working great again so l'm hoping there are not other leaks. I was not here the entire time he did the work so if anything is missing from my description, I'm sure he did it correctly. We'll see how things go and if needed, I'll call him back. Quote Link to comment Share on other sites More sharing options...
BADAIR Posted June 14, 2019 Report Share Posted June 14, 2019 just keep the hares at bay 1 Quote Link to comment Share on other sites More sharing options...