John Dirks Jr Posted July 14, 2014 Report Share Posted July 14, 2014 Could an air filter that is really restricted with dirt cause the system to mis- manage condensate? For instance, the system would be so hungry for air that it would pull a significant amount back through the condensate drain line and thus cause condensate leaks through the system cabinet. Quote Link to comment Share on other sites More sharing options...
Marc Posted July 14, 2014 Report Share Posted July 14, 2014 I've known a few primary drain pans to overflow because of a combination of restriction at the drain opening and blower suction. Shut the thing off and it drains like Niagra Falls. Unusual for sure. Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted July 14, 2014 Author Report Share Posted July 14, 2014 I've known a few primary drain pans to overflow because of a combination of restriction at the drain opening and blower suction. Shut the thing off and it drains like Niagra Falls. Unusual for sure. Thanks Marc. I did a bit more searching and found one source that said the evap core freeze up caused by dirty filters can melt off in a manner that bypasses the drain pan. That could do it too I suppose. Quote Link to comment Share on other sites More sharing options...
Marc Posted July 15, 2014 Report Share Posted July 15, 2014 Its common here. When it freezes up, the ice can expand beyond the dimensions of the pan which means that when it melts the ice water misses the pan and floods the bottom of the air handler (for horizontal flow units). The insulation at the bottom gets wet and will never insulate well again, even after it dries. In the summer season, you can identify the ones with a history of freezing up by the condensate dripping from the bottom 2 inches of the AH. Marc Quote Link to comment Share on other sites More sharing options...
inspector57 Posted July 15, 2014 Report Share Posted July 15, 2014 Yes, John, dirty filters can cause both overflows and freeze ups. Was this coil on the pressure side or the suction side of the fan? Quote Link to comment Share on other sites More sharing options...
Tom Raymond Posted July 15, 2014 Report Share Posted July 15, 2014 This is what the aftermath looks like. Dirty filter. Frozen coil. Primary drain was a pump, it failed. No secondary drain. Click to Enlarge 46.72 KB Who puts a pump on an overhead unit? Knucklehead. Quote Link to comment Share on other sites More sharing options...
John Dirks Jr Posted July 15, 2014 Author Report Share Posted July 15, 2014 Yes, John, dirty filters can cause both overflows and freeze ups. Was this coil on the pressure side or the suction side of the fan? The coil was on the pressure side as usual. Quote Link to comment Share on other sites More sharing options...