Yesterday, during a pre-drywall new construction inspection, I noticed that the framed window opening headers were 2 x 4's instead of 2 x 6's or 2 x 8's. The wall thickness is six inches, so there are three 2 x 4's in each header. 

Since this is the first time I've seen this, I wonder if any of my fellow home inspectors have run across this and found it to be an approved practice?

Thanks in advance for any input.

 

 

IMG_20190922_131722.jpg

Share this post


Link to post
Share on other sites
6 minutes ago, Tom Raymond said:

The actual header is likely at the rim joist.

Did you pull back any insulation?

How would the ceiling load be transferred to a rim joist on a TIJ ceiling?

Take a look at Table R 502.5(1).

Edited by Marc

Share this post


Link to post
Share on other sites
6 minutes ago, Marc said:

How would the ceiling load be transferred to a rim joist on a TIJ ceiling?

(I was trying to put that together in my head as well...)

Edited by mgbinspect

Share this post


Link to post
Share on other sites

Joist hangers. By moving the header into the platform you create room for installation. Especially important if you're going to rely on inefficient fiberglass. 

Share this post


Link to post
Share on other sites
Just now, mgbinspect said:

Back to the subject - has anyone run across this? I think it's panelized construction.

I've never seen wall headers any smaller than 2X6 in my 'unsophisticated' area.

  • Like 1

Share this post


Link to post
Share on other sites

Nothing in the code says that the header has to be at the top of the window. There is no prohibition of placing it in the platform assembly. In fact, the TJI manuals typically detail several options for doing exactly that. 

Share this post


Link to post
Share on other sites

Supporting roof, ceiling, and one center bearing floor, the IRC says that 2 2x4's can span 27 inches. with a 50# snow load. Where you are, they can span 32 inches.

 3 2x4's aren't in the chart but they're likely up to that task. Look at the plans. 

Share this post


Link to post
Share on other sites
21 hours ago, Chad Fabry said:

3 2x4's aren't in the chart but they're likely up to that task. Look at the plans. 

 

I deduced that was probably the case as well. It was just a first for me, so I thought I'd bounce it off all you braniacs. Thanks for the input.

Edited by mgbinspect

Share this post


Link to post
Share on other sites
On 9/23/2019 at 8:35 AM, Marc said:

I've never seen wall headers any smaller than 2X6 in my 'unsophisticated' area.

Me either, which is why this was a curveball.

Share this post


Link to post
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Sign in to follow this  

×
×
  • Create New...