Why? Assuming the OCP device is sized to protect the circuit conductors.

The NEC states that the OCD is "not to exceed" 150% of the rated current. 422.11(E)(3) At 208 volts, that current would be 24.4 amps. The next standard size breaker is 25, which is the only one allowed in this scenario.